Hi everyone!

I going use Inverter for drive pump motor of power 90kW.

In the Mitsubishi short description letter write down that the model FR-F740-01800 drive motor rated capacity 90 kW at 120% overload capacity.

May I use this model of Inverter for drive motor 90 kW?
 
Old Dec 7, 2005 | 04:02 PM
  #2  
Sanguinius's Avatar
Super Moderator
Joined: Mar 2005
Posts: 4,874
From: Norfolk, VA
Default RE: Power of Inverter FR-F700

Just going by the #'s you put up in the post I'd say you CAN use it BUT you'll be pushing it to the limit. The 120% is meant for a protection buffer in case of a spike. Running it at the high limit like that will probably cause it to wear out quicker. I'd recommend trying to find a bit higher of a rating just to save the hassle and the $ of constant replacement. That's just my thoughts on the whole idea.
 